[Beowulf] UPS system for Linux cluster

Many of your questions may have already been answered in earlier discussions or in the FAQ. The search results page will indicate current discussions as well as past list serves, articles, and papers.

Search

Gus Correa gus at ldeo.columbia.edu
Thu Apr 30 09:21:27 PDT 2009


Hi Vlad

A less convenient alternative is to use a few/several smaller
rackmount UPSs, and split the cluster load across them.
They are available in 6-10kVA range from many brands,
single phase input (maybe three-phase also), typically in 3U units.
If you have a site generator, you may not need a lot of battery time,
which is our case here.
The bad news is that rackmount UPSs take a lot of rack space,
and if you need many it may not be cost effective.
We had to (reluctantly) use this solution, which I hope is temporary,
because our site large UPSs were maxed out.

Previous discussions that may be of interest:

http://www.beowulf.org/archive/2009-January/024408.html
http://www.beowulf.org/archive/2009-April/025047.html
http://www.beowulf.org/archive/2009-April/024997.html

Gus Correa
---------------------------------------------------------------------
Gustavo Correa
Lamont-Doherty Earth Observatory - Columbia University
Palisades, NY, 10964-8000 - USA
---------------------------------------------------------------------

Tom Pierce wrote:
> Dear Vlad,
> 
> I did a similar project last fall. The only unpleasant surprise is
> that most UPS are capable of running continuously at 80% of their kVA
> value.   So you may want a larger system.
> 
> You can get more current when you go to a three phase UPS system.
> 
> 
> On Wed, Apr 29, 2009 at 7:46 AM,  <vlad at geociencias.unam.mx> wrote:
>> Hi,
>>
>> I have a linux cluster and need to purchase a UPS system.
>> The total expected current consumption will be 240 amps. At 120 V this
>> would require a 30 kVA UPS system.
>> However, I see that 30 kVA systems have a limitation for the input
>> current. For example, this 30 kVA system
>> (http://www.provantage.com/tripp-lite-su30k3-3xr5~7TRPL1Q9.htm) allows
>> only 90 amps as input
>> current. I am a bit confused here, and I need some advice on what UPS
>> system I should look for.
>>
>> Thanks,
>> Vlad
>>