Archives


- Beowulf
- Beowulf Announce
- Scyld-users
- Beowulf on Debian

[Beowulf] Emergency Power Off

Many of your questions may have already been answered in earlier discussions or in the FAQ. The search results page will indicate current discussions as well as past list serves, articles, and papers.

Search

Robert G. Brown rgb at phy.duke.edu
Sun Mar 18 10:36:50 PDT 2007


On Sun, 18 Mar 2007, Jim Lux wrote:

> At 06:52 AM 3/18/2007, Robert G. Brown wrote:
>> To answer my own question (GIYF, after all:-) there is a white paper
>> here:
>> 
>> HOWEVER, if you love your local firemen and want them to live (or love
>> yourselves and the other employees who sit near the data not-a-centers),
>> the same white paper says that an EPO switch is still a very good idea
>> for small server rooms and wiring closets that are not "data centers"
>> but are just "data closets" or "data rooms that aren't quite centers".
>
> Do not underestimate the power of lobby...  e.g. The front matter of the IEEE 
> Emerald Book, (which used to be called "grounding for sensitive electronic 
> equipment") explains why the "sensitive" was removed.  Mfrs didn't want their 
> particular piece of equipment to be referred to as sensitive.
>
> There's a huge "small office and retail" sort of market for middling sized 
> UPSes, and APC and the like would like to sell into that market as a "plug 
> and play" product.  Also, this is where the local AHJ can play a role.  THEY 
> can say, we don't care if your installation isn't in a room that meets ALL of 
> the requirements of 645, we want you to provide a disconnecting means anyway.

I could wish that they made this a whole lot simpler.  And perhaps
standardized so it would be cheap as well as easy.

> Another way that folks avoid the code is by putting the UPS into a rack with 
> the equipment being powered.  That puts it on the other side  the "line of 
> demarcation" between that which is subject to code and that which is 
> "internal to the equipment" and subject to different rules.  And, here, the

Hooo.  Right.  So the firefighters won't get electrocuted by big UPS's
IN a rack, only by smaller UPS's on the floor.

Makes perfect sense.  Sure.

I'm going to try to figure out how to put an EPO in this room for less
than a fortune, even though I'm pretty sure that it isn't strictly
required.  Even if it is just one that controls the UPS's -- so that
the building power can be cut externally and one can bop off the UPS's
on entering the room.

The building power is tricky enough as it is -- they have a gas
generator that kicks in transparently on loss of grid power (it's a
medical clinic).  That is not my thing, though.

    rgb

-- 
Robert G. Brown	                       http://www.phy.duke.edu/~rgb/
Duke University Dept. of Physics, Box 90305
Durham, N.C. 27708-0305
Phone: 1-919-660-2567  Fax: 919-660-2525     email:rgb at phy.duke.edu





More information about the Beowulf mailing list